FM200 residue is mostly all of the gunk and grease in the pipes left over from their manufacture and threaded-metal-fitting assembly.
John
> On 14 Dec 2018, at 4:31 am, Bevan Slattery <bevan at slattery.net.au> wrote:
> 
> It’s pretty much all been said.
> 
> Halon (long gone).  Reaction sucks oxygen out of air.
> FM200 (safe but being phased out).  Heard it can leave a residue despite the brochure saying not.
> Inergen  more common (and others like it).  Fundamentally mostly nitrogen that drops oxygen below 15% and drops temperature.  These are two components of a fire (heat, fuel and oxygen).  People can operate comfortably below 15% oxygen.  In fact at 10% you can still function more than enough to pick up your gear and leave the room.
> 
> I did quite a bit of research on reduced oxygen environments (hypoxic) which is used on (Firepass etc.) http://www.firepass.com/oxygen-reduction-fire 
> 
> Obviously dry pipe is used a lot. The issues with gas suppression today are more around noise (and vibration) and temp drop and they relate to spinning disks and circuit boards, more than people.
> 
> The issues around dry pipe is, well when it goes off, it’s not very dry and water/equipment certainly doesn’t mix.
> 
> Cheers
> 
> B
> 
> From: AusNOG <ausnog-bounces at lists.ausnog.net> on behalf of Paul Wilkins <paulwilkins369 at gmail.com>
> Sent: Wednesday, December 12, 2018 3:53 pm
> To: AusNOG at lists.ausnog.net
> Subject: [AusNOG] [AUSNog] : Re Data Centre Fire Suppression Safety
>  
> Every data centre has a fire suppression system. We're not used to thinking of this as a hazardous environment, but consequent totwo techs being found dead working on a fire suppression system in Antarctica, I find myself wondering yet again, why there aren't more stringent controls around the fire suppression systems in data centres: viz - when you enter a data centre, how confident can you be you're not going to be quietly asphyxiated?
> 
> Kind regards
> 
> Paul Wilkins
> 
> _______________________________________________
> AusNOG mailing list
> AusNOG at lists.ausnog.net
> http://lists.ausnog.net/mailman/listinfo/ausnog
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.ausnog.net/pipermail/ausnog/attachments/20181214/9d5c1650/attachment.html>
    
    
More information about the AusNOG
mailing list