[AusNOG] Question about hardware spec for a DC
Paul Gear
ausnog at libertysys.com.au
Thu Apr 24 13:25:44 EST 2014
Good point. Because you can never be sure that the remaining PS is not
going to fail, it needs a maintenance window regardless. I would expect
that the probability of a PS failing would go up if its load is
dramatically increased, which is exactly what would happen if the other
PS input was removed.
Paul
On 04/24/2014 12:15 PM, Colin Stubbs wrote:
>
> I once thought like that too.
>
> But if you're re-organising power and yanking cables out and plugging
> them back in on anything other than a lab system you should be working
> within a declared maintenance window anyway.
>
> There's too much risk that something will come out that shouldn't, or
> that something will shift just enough to cause a problem.
>
> It might be acceptable to do it without a window for a UAT/test/dev
> system but anything revenue generating or revenue supporting... hell no.
>
> Having the convenience and ability to re-arrange power cables at any
> time of day without risk and loss of $'s stems from designing systems to
> cope with failure to start with.
>
> That may in small part be because you put two PSU's in the boxes; but it
> won't be the only reason.
>
> -Colin
>
> On 24 April 2014 11:30, Paul Gear <ausnog at libertysys.com.au
> <mailto:ausnog at libertysys.com.au>> wrote:
>
> In my judgement, the big benefit of dual power supplies
> (particularly on servers, switches, & routers) is that it enables
> reorganising of power circuits in racks without requiring a downtime
> window. Like you say, a comprehensive view of high availability
> means designing N + 1 redundancy at the system level, but dual power
> supplies to those N + 1 devices is a big convenience factor.
>
> Paul
>
>
> On 04/24/2014 11:25 AM, Colin Stubbs wrote:
>> IMHO
>>
>> Avoid that auto power-transfer stuff in rack if you can. Those
>> devices are best used only for low end boxes like NTU's/etc with
>> which you can only ever install/utilise a single box at a time.
>>
>> Buy equipment which has dual PSU's as an option in preference, but
>> don't mandate it or mandate buying the two power supplies.
>> Mandating it will just mean you're wasting part of your budget
>> unnecessarily on every single purchase as you may force yourself
>> to buy bigger boxes than required; and/or buy more PSU's than you
>> need.
>>
>> Avoid *depending* on dual PSU's if you can, e.g. don't design
>> anything with the assumption having two power supplies in a box
>> will keep everything working if there is a loss of power or if one
>> of the PSU's fails.
>>
>> Design for failure with N+1 redundancy at a system level, e.g.
>> install two or more of every box and use them in active/active or
>> active/standby capacities. If you do that you won't necessarily
>> require two power supplies in each to achieve a very high level of
>> availability.
>>
>> Choose to use dual PSU's primarily based on the location and the
>> power infrastructure available, in combination with how many boxes
>> you have. e.g. if you're in a crappy DC where they can't deliver
>> access to two genuinely independent sources of power the value of
>> having two PSU's is greatly reduced regardless of how many many
>> boxes you've installed.
>>
>> Read up on HA concepts if you're not sure what you need or why.
>>
>> 13 years old now but this book is still handy and the concepts
>> still hold true,
>>
>> http://www.ciscopress.com/store/high-availability-network-fundamentals-9781587130175
>>
>
>
> _______________________________________________
> AusNOG mailing list
> AusNOG at lists.ausnog.net <mailto:AusNOG at lists.ausnog.net>
> http://lists.ausnog.net/mailman/listinfo/ausnog
>
>
More information about the AusNOG
mailing list