<div dir="ltr"><div dir="ltr"><div><p class="gmail-">Based on previous experience in power distribution design, here’s my general approach to derating power circuits:</p><p>
</p><p class="gmail-"><b><u>Disclaimer: Always refer to AS/NZS 3000, AS/NZS 3008, and consult a licensed electrician for all practical installations and compliance.</u></b></p><p>For ambient temperatures around 40°C, a thermal derating factor of 0.87 is typically used (based on AS/NZS 3000/3008).<br><br>Real-world usable power also depends on:<br>The power factor (PF) of the connected equipment.<br><br>Whether the PDU is installed in a hot aisle or cold aisle.<br>If the load is continuous, you must also apply the 80% continuous load rule as per AS/NZS 3000.<br><br>Example — 30A Circuit @ 230V<br>Cold Aisle Scenario (23°C, PF = 0.9):<br>No temperature derating needed at 23°C.<br><br>Apply 80% derating for continuous load:<br>30A × 0.8 = 24A usable<br><br>Real usable power:<br>24A × 230V × 0.9 = 4968 W<br><br>Usable continuous load = ~4968W<br>Peak load capacity (non-continuous):<br>30A × 230V × 0.9 = 6210 W<br>(for short-term bursts only)<br><br>Hot Aisle Scenario (40°C, PF = 0.8):<br>Apply both continuous and thermal derating:<br>30A × 0.8 (continuous) × 0.87 (thermal) = 20.88A<br><br>Real usable power:<br>20.88A × 230V × 0.8 = 3848 W<br><br>Usable continuous load = ~3848W<br>Cold Aisle (23°C)        24A     0.9     4968 W<br>Hot Aisle (40°C)       20.88A  0.8     3848 W<br></p></div><div><br></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Tue, Apr 8, 2025 at 2:48 PM Alex Samad <<a href="mailto:alex@samad.com.au" target="_blank">alex@samad.com.au</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div dir="ltr"><div class="gmail_quote"><div dir="ltr"><div>Hi</div><div><br></div><div>I'm having the pleasure of looking at PDU's and trying to standardise over US / UK / Japan / Aus <br></div><div><br></div><div>Something I didn't know was the standard in the US for derating electrical devices. whilst I normally plan for max normal draw of around 80% of rating. seems like PDU for USA have a derating value.</div><div><br></div><div>So I am seeing 30amp @ 230v in and line rating of 24amp and max 30amp.  The notes seems to suggest you can go over 24 amps but only for a very short period of time - seems like minutes.</div><div><br></div><div>This seems a bit of a pain for me - whilst I wouldn't normally run over the 24 amps there have been times i have had to run over - but under 30 for days if not a couple of weeks.</div><div><br></div><div>Currently I'm trying to order into japan (omg), lot of their stuff is imported which means it comes with the USA specs.  so 24/30 amp setup.. Interestingly also noted that when you read the fine prints its actually 2 x 20amp breakers - 1 breaker per bank .. PDU has 2 banks <br></div><div><br></div><div>I can't find anything about derating for Aus - do we not do it in Aus or mandate it ?<br></div><div><br></div><div><br></div><div>Alex<br></div></div>
</div></div>
_______________________________________________<br>
AusNOG mailing list<br>
<a href="mailto:AusNOG@lists.ausnog.net" target="_blank">AusNOG@lists.ausnog.net</a><br>
<a href="https://lists.ausnog.net/mailman/listinfo/ausnog" rel="noreferrer" target="_blank">https://lists.ausnog.net/mailman/listinfo/ausnog</a><br>
</blockquote></div>
</div>