[AusNOG] Vocus Datacentre outage.

Mark Dignam mark at innaloo.net
Tue Mar 14 13:23:07 AEDT 2023


Something that I have to keep reminding beancounters with A/B planning is don’t go above 40% load on either side.

 

Its very difficult to convince a CFO who’s entire life is spent with a spreadsheet open in front of him is that N+1 means typically Double, and that Kw != Kva.

 

 

From: AusNOG <ausnog-bounces at lists.ausnog.net> On Behalf Of Matt Perkins
Sent: Tuesday, March 14, 2023 9:18 AM
To: Christopher Hawker <chris at thesysadmin.dev>; Nathan Brookfield <Nathan.Brookfield at iperium.com.au>; ausnog at lists.ausnog.net
Subject: Re: [AusNOG] Vocus Datacentre outage.

 

The questions left to be answered for Vocus is why did it take 12 hours to restore one rail. Where was the static bypass and failing that where was the maintenance bypass.  Im guessing that's what it's on maintenance bypass now and the slow action may have something to do with the public holiday in Vic..  

 

I shouldn't speculate. But it is fun. 

 

 Something seriously let go in that UPS. If i had to put my electrical engineers hat on I would say their load capacitor maintenance was not done and let go. Or someone was working upstream and broke the natural/earth bond. But there's a lot of parts in a system like that , most modern DC UPS setups are fairly robust.  I once had 3 strings of batteries catch fire and melt down and the UPS didn't miss a beat other then spewing a lot of alarms. We moved strings around on the fly and nobody even noticed.   

 

The other things that seems odd is why did an A failure trip B.  Sounds like a single supply is at surge/break capacity. Also a worry.  

 

But in the end we all have redundancy around 530 Collins right ? Right ? 

 

Matt

 

 

On 14/3/2023 11:50 am, Christopher Hawker wrote:

SY1 apparently experienced a full power outage back in July 2009, according to AusNOG Archives. Some reported full outages, some partial. Was not a DC fault though, looks like a much larger grid issue where a fault at the Bayswater Power Station in the Hunter Valley (which affected generators in QLD and VIC) caused about 1000MW to be dropped from the grid, resulting in rolling blackouts across QLD, NSW, TAS, SA and VIC.

 

https://lists.ausnog.net/pipermail/ausnog/2009-July/003222.html

 

CH.

  _____  

From: AusNOG  <mailto:ausnog-bounces at lists.ausnog.net> <ausnog-bounces at lists.ausnog.net> on behalf of Nathan Brookfield  <mailto:Nathan.Brookfield at iperium.com.au> <Nathan.Brookfield at iperium.com.au>
Sent: Tuesday, March 14, 2023 11:40 AM
To: Matt Perkins  <mailto:matt at spectrum.com.au> <matt at spectrum.com.au>; ausnog at lists.ausnog.net <mailto:ausnog at lists.ausnog.net>   <mailto:ausnog at lists.ausnog.net> <ausnog at lists.ausnog.net>
Subject: Re: [AusNOG] Vocus Datacentre outage. 

 

Have 100% had A and B fail separately at SY1 but never both, thankfully!!!

 

Could have been part of the facility though so don’t quote me.

 

UK on the other hand, fail!

 

From: Matt Perkins  <mailto:matt at spectrum.com.au> <matt at spectrum.com.au> 
Sent: Tuesday, 14 March 2023 11:30 AM
To: Nathan Brookfield  <mailto:Nathan.Brookfield at iperium.com.au> <Nathan.Brookfield at iperium.com.au>; ausnog at lists.ausnog.net <mailto:ausnog at lists.ausnog.net> 
Subject: Re: [AusNOG] Vocus Datacentre outage.

 

SY1 had A or B fail a few years back if my memory serves me correctly.  But I was referring  London and Manchester which both had total outages in recent years. 

Matt.

 

On 14/3/2023 11:26 am, Nathan Brookfield wrote:

I’ve never had an A+B power rail failure at Equinix in 18 years I’ve been in there facilities, TOUCH WOOD!!!

 

Nathan Brookfield | VK2NAB
General Manager

p: 1300 592 330 | m: 0412 266 008
e: Nathan.brookfield at iperium.com.au <mailto:Nathan.brookfield at iperium.com.au>  | w: iperium.com.au

Suite 4.02, 189 Kent Street Sydney NSW 2000


Your Telco Team

DISCLAIMER: This document is intended solely for the named addressee. This electronic communication, which includes any files or attachments thereto, contains proprietary or confidential information and may be privileged and otherwise protected under copyright or other applicable intellectual property laws. The use, disclosure, copying or distribution of any of the information contained in this document, by any person other than the addressee, is strictly prohibited. If you received this document in error, please contact the sender immediately and delete all the material from any computer. Confidentiality and legal privilege are not waived or lost by reason of mistaken delivery to you. Any views or opinions presented are solely those of the author and do not necessarily represent those of Iperium. 

WARNING: Computer viruses can be transmitted via email. The recipient should check this email and any attachments for the presence of viruses. Iperium accepts no liability for any damage caused by any virus transmitted by this email.

From: AusNOG  <mailto:ausnog-bounces at lists.ausnog.net> <ausnog-bounces at lists.ausnog.net> On Behalf Of Matt Perkins
Sent: Tuesday, 14 March 2023 11:18 AM
To: ausnog at lists.ausnog.net <mailto:ausnog at lists.ausnog.net> 
Subject: Re: [AusNOG] Vocus Datacentre outage.

 

Yea because Eqinix has never had a power outage. :) 

I think it's a little premature to judge at the moment. Doesn't sound good based on the current info but we have all had bad days im sure.  

Matt

 

On 14/3/2023 11:06 am, Bradley Amm wrote:

Friends like let friends put gear in a Vocus dtacenter. Only NextDC or Equinix :) 

Sent from my iPhone





On 14 Mar 2023, at 7:08 am, DaZZa  <mailto:dazzagibbs at gmail.com> <dazzagibbs at gmail.com> wrote:

 

Doesn't say a whole lot about Vocus' data center design methodology, nor their periodic contingency testing.

 

They're apparently replacing the entire UPS on Friday - guess we can all expect more outages then when they stuff that up.

 

D

 

On Mon, 13 Mar 2023 at 18:30, Chad Kelly <chad at cpkws.com.au <mailto:chad at cpkws.com.au> > wrote:

Thought I would create a new thread on this, as the issue wasn’t related to AussieBB. 

It is looking like this Melbourne outage is similar to the Sydney outage back in 2018, in that it appears to have been yet again caused by an issue with their UPS systems yet again.

I’ll leave this hear https://www.arnnet.com.au/article/633314/servers-australia-uproots-services-after-vocus-data-centre-outage/ and this article on today’s outage as well. 

https://www.itnews.com.au/news/vocus-melbourne-data-centre-hit-by-power-outage-591987

 

Regards Chad. 

 

 

 

Chad Kelly 

Manager 

CPK Web Services 

Phone 03 52730246

Web https://www.cpkws.com.au

<image001.jpg>

 

_______________________________________________
AusNOG mailing list
AusNOG at lists.ausnog.net <mailto:AusNOG at lists.ausnog.net> 
https://lists.ausnog.net/mailman/listinfo/ausnog



-- 

veg·e·tar·i·an:
Ancient tribal slang for the village idiot who can't hunt, fish or ride

_______________________________________________
AusNOG mailing list
AusNOG at lists.ausnog.net <mailto:AusNOG at lists.ausnog.net> 
https://lists.ausnog.net/mailman/listinfo/ausnog





_______________________________________________
AusNOG mailing list
AusNOG at lists.ausnog.net <mailto:AusNOG at lists.ausnog.net> 
https://lists.ausnog.net/mailman/listinfo/ausnog

-- 
** DO NOT SEND PRIVATE OR CONFIDENTIAL MATERIAL VIA EMAIL 
 
/* Matt Perkins
        Direct 02 8916 8101     Spectrum Networks Ptd. Ltd.
        Office 1300 133 299     matt at spectrum.com.au <mailto:matt at spectrum.com.au> 
        ABN 66 090 112 913      Level 6, 350 George Street Sydney 2000
 
*/

-- 
** DO NOT SEND PRIVATE OR CONFIDENTIAL MATERIAL VIA EMAIL 
 
/* Matt Perkins
        Direct 02 8916 8101     Spectrum Networks Ptd. Ltd.
        Office 1300 133 299     matt at spectrum.com.au <mailto:matt at spectrum.com.au> 
        ABN 66 090 112 913      Level 6, 350 George Street Sydney 2000
 
*/

-- 
** DO NOT SEND PRIVATE OR CONFIDENTIAL MATERIAL VIA EMAIL 
 
/* Matt Perkins
        Direct 02 8916 8101     Spectrum Networks Ptd. Ltd.
        Office 1300 133 299     matt at spectrum.com.au <mailto:matt at spectrum.com.au> 
        ABN 66 090 112 913      Level 6, 350 George Street Sydney 2000
 
*/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://lists.ausnog.net/pipermail/ausnog/attachments/20230314/a8cb5a33/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 4595 bytes
Desc: not available
URL: <https://lists.ausnog.net/pipermail/ausnog/attachments/20230314/a8cb5a33/attachment.png>


More information about the AusNOG mailing list