[AusNOG] Vocus Datacentre outage.
    Matt Perkins 
    matt at spectrum.com.au
       
    Tue Mar 14 12:17:46 AEDT 2023
    
    
  
The questions left to be answered for Vocus is why did it take 12 hours 
to restore one rail. Where was the static bypass and failing that where 
was the maintenance bypass.  Im guessing that's what it's on maintenance 
bypass now and the slow action may have something to do with the public 
holiday in Vic..
I shouldn't speculate. But it is fun.
  Something seriously let go in that UPS. If i had to put my electrical 
engineers hat on I would say their load capacitor maintenance was not 
done and let go. Or someone was working upstream and broke the 
natural/earth bond. But there's a lot of parts in a system like that , 
most modern DC UPS setups are fairly robust.  I once had 3 strings of 
batteries catch fire and melt down and the UPS didn't miss a beat other 
then spewing a lot of alarms. We moved strings around on the fly and 
nobody even noticed.
The other things that seems odd is why did an A failure trip B. Sounds 
like a single supply is at surge/break capacity. Also a worry.
But in the end we all have redundancy around 530 Collins right ? Right ?
Matt
On 14/3/2023 11:50 am, Christopher Hawker wrote:
> SY1 apparently experienced a full power outage back in July 2009, 
> according to AusNOG Archives. Some reported full outages, some 
> partial. Was not a DC fault though, looks like a much larger grid 
> issue where a fault at the Bayswater Power Station in the Hunter 
> Valley (which affected generators in QLD and VIC) caused about 1000MW 
> to be dropped from the grid, resulting in rolling blackouts across 
> QLD, NSW, TAS, SA and VIC.
>
> https://lists.ausnog.net/pipermail/ausnog/2009-July/003222.html
>
> CH.
> ------------------------------------------------------------------------
> *From:* AusNOG <ausnog-bounces at lists.ausnog.net> on behalf of Nathan 
> Brookfield <Nathan.Brookfield at iperium.com.au>
> *Sent:* Tuesday, March 14, 2023 11:40 AM
> *To:* Matt Perkins <matt at spectrum.com.au>; ausnog at lists.ausnog.net 
> <ausnog at lists.ausnog.net>
> *Subject:* Re: [AusNOG] Vocus Datacentre outage.
>
> Have 100% had A and B fail separately at SY1 but never both, thankfully!!!
>
> Could have been part of the facility though so don’t quote me.
>
> UK on the other hand, fail!
>
> *From:*Matt Perkins <matt at spectrum.com.au>
> *Sent:* Tuesday, 14 March 2023 11:30 AM
> *To:* Nathan Brookfield <Nathan.Brookfield at iperium.com.au>; 
> ausnog at lists.ausnog.net
> *Subject:* Re: [AusNOG] Vocus Datacentre outage.
>
> SY1 had A or B fail a few years back if my memory serves me 
> correctly.  But I was referring  London and Manchester which both had 
> total outages in recent years.
>
> Matt.
>
> On 14/3/2023 11:26 am, Nathan Brookfield wrote:
>
>     I’ve never had an A+B power rail failure at Equinix in 18 years
>     I’ve been in there facilities, TOUCH WOOD!!!
>
>     *Nathan Brookfield | VK2NAB
>     *General Manager
>
>     *p*: 1300 592 330 | *m*: 0412 266 008
>     *e*: Nathan.brookfield at iperium.com.au | *w*: iperium.com.au
>
>     Suite 4.02, 189 Kent Street Sydney NSW 2000
>
>
>     *Your Telco Team*
>
>     DISCLAIMER: This document is intended solely for the named
>     addressee. This electronic communication, which includes any files
>     or attachments thereto, contains proprietary or confidential
>     information and may be privileged and otherwise protected under
>     copyright or other applicable intellectual property laws. The use,
>     disclosure, copying or distribution of any of the information
>     contained in this document, by any person other than the
>     addressee, is strictly prohibited. If you received this document
>     in error, please contact the sender immediately and delete all the
>     material from any computer. Confidentiality and legal privilege
>     are not waived or lost by reason of mistaken delivery to you. Any
>     views or opinions presented are solely those of the author and do
>     not necessarily represent those of Iperium.
>
>     WARNING: Computer viruses can be transmitted via email. The
>     recipient should check this email and any attachments for the
>     presence of viruses. Iperium accepts no liability for any damage
>     caused by any virus transmitted by this email.
>
>     *From:*AusNOG <ausnog-bounces at lists.ausnog.net>
>     <mailto:ausnog-bounces at lists.ausnog.net> *On Behalf Of *Matt Perkins
>     *Sent:* Tuesday, 14 March 2023 11:18 AM
>     *To:* ausnog at lists.ausnog.net
>     *Subject:* Re: [AusNOG] Vocus Datacentre outage.
>
>     Yea because Eqinix has never had a power outage. :)
>
>     I think it's a little premature to judge at the moment. Doesn't
>     sound good based on the current info but we have all had bad days
>     im sure.
>
>     Matt
>
>     On 14/3/2023 11:06 am, Bradley Amm wrote:
>
>         Friends like let friends put gear in a Vocus dtacenter. Only
>         NextDC or Equinix :)
>
>         Sent from my iPhone
>
>
>
>
>             On 14 Mar 2023, at 7:08 am, DaZZa <dazzagibbs at gmail.com>
>             <mailto:dazzagibbs at gmail.com> wrote:
>
>             
>
>             Doesn't say a whole lot about Vocus' data center design
>             methodology, nor their periodic contingency testing.
>
>             They're apparently replacing the entire UPS on Friday -
>             guess we can all expect more outages then when they stuff
>             that up.
>
>             D
>
>             On Mon, 13 Mar 2023 at 18:30, Chad Kelly
>             <chad at cpkws.com.au> wrote:
>
>                 Thought I would create a new thread on this, as the
>                 issue wasn’t related to AussieBB.
>
>                 It is looking like this Melbourne outage is similar to
>                 the Sydney outage back in 2018, in that it appears to
>                 have been yet again caused by an issue with their UPS
>                 systems yet again.
>
>                 I’ll leave this hear
>                 https://www.arnnet.com.au/article/633314/servers-australia-uproots-services-after-vocus-data-centre-outage/
>                 and this article on today’s outage as well.
>
>                 https://www.itnews.com.au/news/vocus-melbourne-data-centre-hit-by-power-outage-591987
>
>                 Regards Chad.
>
>                 Chad Kelly
>
>                 Manager
>
>                 CPK Web Services
>
>                 Phone 03 52730246
>
>                 Web https://www.cpkws.com.au
>
>                 <image001.jpg>
>
>                 _______________________________________________
>                 AusNOG mailing list
>                 AusNOG at lists.ausnog.net
>                 https://lists.ausnog.net/mailman/listinfo/ausnog
>
>
>
>             -- 
>
>             veg·e·tar·i·an:
>             Ancient tribal slang for the village idiot who can't hunt,
>             fish or ride
>
>             _______________________________________________
>             AusNOG mailing list
>             AusNOG at lists.ausnog.net
>             https://lists.ausnog.net/mailman/listinfo/ausnog
>
>
>
>
>         _______________________________________________
>
>         AusNOG mailing list
>
>         AusNOG at lists.ausnog.net
>
>         https://lists.ausnog.net/mailman/listinfo/ausnog
>
>     -- 
>
>     ** DO NOT SEND PRIVATE OR CONFIDENTIAL MATERIAL VIA EMAIL
>
>       
>
>     /* Matt Perkins
>
>              Direct 02 8916 8101     Spectrum Networks Ptd. Ltd.
>
>              Office 1300 133 299matt at spectrum.com.au
>
>              ABN 66 090 112 913      Level 6, 350 George Street Sydney 2000
>
>       
>
>     */
>
> -- 
> ** DO NOT SEND PRIVATE OR CONFIDENTIAL MATERIAL VIA EMAIL
>   
> /* Matt Perkins
>          Direct 02 8916 8101     Spectrum Networks Ptd. Ltd.
>          Office 1300 133 299matt at spectrum.com.au
>          ABN 66 090 112 913      Level 6, 350 George Street Sydney 2000
>   
> */
-- 
** DO NOT SEND PRIVATE OR CONFIDENTIAL MATERIAL VIA EMAIL
/* Matt Perkins
         Direct 02 8916 8101     Spectrum Networks Ptd. Ltd.
         Office 1300 133 299matt at spectrum.com.au
         ABN 66 090 112 913      Level 6, 350 George Street Sydney 2000
*/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <https://lists.ausnog.net/pipermail/ausnog/attachments/20230314/688896d1/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 4595 bytes
Desc: not available
URL: <https://lists.ausnog.net/pipermail/ausnog/attachments/20230314/688896d1/attachment-0001.png>
    
    
More information about the AusNOG
mailing list