[AusNOG] NextDC Melbourne - Scheduled Power Maintenance - 15th August

James Hodgkinson yaleman at ricetek.net
Thu Aug 10 18:26:45 EST 2017


We have a tech on site tomorrow morning in Brisbane to do live works on
a major DC panel, they need a look out with a torch, insulating matting
and a few other things but it's legal.
James


On Thu, 10 Aug 2017, at 16:04, Sam Silvester wrote:
> I also am unaware of such a law. Simon, can you advise?
> 
> I'm told in QLD that live works are not permitted, but I am in SA so I
> have not really bothered too much to check if that is hearsay or true.> 
> On Thursday, 10 August 2017, Jared Hirst
> <jared.hirst at serversaustralia.com.au> wrote:>> 
>> Hi Simon,
>> 
>> Maybe it could be helpful to the Ausnog list to point us to that law
>> you refer too?>> 
>> As I personally have never heard or seen this done in any DC in
>> Australia, or the world in the past 15 years I have been housing gear
>> in Data Centres.>> 
>> I agree that gear should have 2N, and it doesn’t affect me, but there
>> are people that have equipment that have single fed devices, and I
>> believe you don’t allow self installed STS devices to be installed? I
>> could be wrong.>> 
>> In any case, it would be interesting to see the law the requires you
>> to shut down boards.>> 
>> Regards,
>> 
>>  Jared Hirst
>>  Servers Australia Pty Ltd
>>  Phone: +61 2 8115 8801
>>  Email: jared.hirst at serversaustralia.com.au
>> 
>> *From:* AusNOG <ausnog-bounces at lists.ausnog.net> on behalf of Simon
>> Cooper <spgc at inbox.com> *Sent:* Thursday, August 10, 2017 8:39:13 AM
>> *To:* ausnog at lists.ausnog.net *Subject:* Re: [AusNOG] NextDC
>> Melbourne - Scheduled Power Maintenance - 15th August>>  
>> Thanks guys, appreciate the feedback.
>> 
>> At NEXTDC we work very hard to keep critical infrastructure
>> maintenance that impacts racks or the environment within the data
>> hall to an absolute minimum.>> 
>> However, some works are required to happen from time to time by law
>> and one of those activities is a de-energisation and inspection of
>> each of our major switchboards.  This is all about ensuring that the
>> electrical system is safe, and is an unavoidable piece of work.
>> Rightly so.>> 
>> Every rack in a NEXTDC data centre has 2N power feeds offered to it,
>> and we highly recommend that they are used for every device in the
>> rack.  This occasional maintenance is one of the many reasons we
>> provide this capability.  Any device using the 2N supplies (aka A & B
>> feeds) will simply see its power swing from one feed to the other.
>> Any rack that is drawing no more that its contracted power level will
>> have no issue when all devices move from A to B or vice versa.>> 
>> Our notifications were made well in advance, as we want to give
>> customers time to consider the management of these works and we don't
>> assume that every rack is perfectly deployed:  We are here 24/7 to
>> assist customers with rack inspections or specific circuit down tests
>> or maybe a controlled move prior to the day (e.g. for devices that
>> are single fed).>> 
>> Also, as we work though those discussions with customers we
>> understand the timing in relation to their businesses, and we work
>> very hard to coordinate schedules despite each switch board
>> supporting many different customers and customer instances across the
>> data centre.  Occasionally that means we have to make a difficult
>> decisions which may result in schedule changes.  When that does
>> happen, we do not compromise our notification periods.>> 
>> I'll be happy to discuss these works with anyone - probably best
>> offline or on the phone - but trust me when I say we are doing our
>> absolute best to keep your data centre operating safely and reliably
>> for many years to come.>> 
>> Thanks,
>> Simon
>> COO, NEXTDC
>> 
>>> -----Original Message-----
>>> *From:* nathan at nightsys.net
>>> *Sent:* Thu, 10 Aug 2017 05:39:02 +1000
>>> *To:* shaun at rackcentral.com
>>> *Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power
>>> Maintenance - 15th August>>> 
>>> This seems reasonable? As long as no single Data Hall has both A and
>>> B feeds removed simultaneously, that seems normal. Doing B on Hall 2
>>> and A on Hall 3 on the same day does seem slightly adventurous, but
>>> not entirely unreasonable (mostly in terms of if something goes bad
>>> in both, staff get stretched thin remediating issues).>>> 
>>> A and B feeds are designed to provide redundancy to equipment,
>>> allowing one feed to fail and systems to continue on the other.
>>> Anything mission critical should be able to draw from either feed as
>>> required (dual PSU), and if there is a power deficit on one feed
>>> (causing circuits to trip), that would imply the circuits are
>>> incorrectly sized?>>> 
>>> In addition, anything mission critical with a single power supply
>>> would be on an ATS you would assume, or a pair of equivalent devices
>>> installed with one on each rail?>>> 
>>> Things break in datacentres, planned maintenance happens sometimes,
>>> better than no maintenance at all :) The fact they are notifying you
>>> is better than not, and it being scheduled is probably still better
>>> than unscheduled :) (easier to ensure sufficient staffing to keep a
>>> close eye on things)>>> 
>>> Nathan.
>>> 
>>> On Wed, Aug 9, 2017 at 3:43 PM, Shaun McGuane
>>> <shaun at rackcentral.com> wrote:>>> 
>>>> Here is the entire scheduled maintenance windows for all the halls
>>>> we occupy.____>>>> __ __


>>>> DataHall 2____


>>>> A Feed - Tuesday 8th August 2017 07:00 UTC +10 until 16:00 UTC +10.
>>>> B Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC
>>>> +10.____>>>> __ __


>>>> DataHall 3____


>>>> A Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC +10
>>>> B Feed - Monday 14th August 2017 07:00 UTC +10 until 16:00 UTC
>>>> +10____>>>> __ __


>>>> DataHall 4____


>>>> 
>>>> B Feed - Tuesday 15th August 2017 07:00 UTC +10 until 16:00 UTC
>>>> +10.____>>>> __ __


>>>> 
>>>> __·         __So looks like no power on 3 data halls B feeds on the
>>>> same day. ____>>>> __·         __Data Hall 2 was scheduled for A rail on the 8th of
>>>> August but has been re-scheduled with no new date of works.____>>>> __·         __Data Hall 3 was scheduled for A rail on the ____


>>>> __ __


>>>> Problem is that I have 3x separate dates on 3 separate e-mails for
>>>> Data Hall 3 and I have requested a revised clarification ____>>>> Just now on the above as there has already been re-schedules for
>>>> Data Hall 2 and 3.____>>>> __ __


>>>> This feels like it’s going sideways and it has not even
>>>> started.____>>>> __ __


>>>> Regards____


>>>> Shaun____


>>>> __ __


>>>> __ __


>>>> *From:* AusNOG [mailto:ausnog-bounces at lists.ausnog.net] *On Behalf
>>>> Of *Murat Sener *Sent:* Wednesday, 9 August 2017 3:20 PM *To:*
>>>> Matthew VK3EVL <hitman at itglowz.com>; ausnog at lists.ausnog.net>>>> 
>>>> *Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power
>>>> Maintenance - 15th August____>>>> 


>>>> __ __


>>>> We have been told only Feed B in Data hall 2 will be effected as
>>>> per original schedule and Feed A is yet to be rescheduled.____>>>> __ __


>>>> __ __


>>>> __ __


>>>>  ____


>>>> *Murat Sener*     Datacentre Manager____


>>>> *PREMIER* Technology Solutions *P. *1300 76 76 48    *F. *1300 76
>>>> 76 49    *M. *0450 604 350 ____>>>> __ __


>>>> *How am I doing? Let us know!* SIMPLY CLICK ON A FACE TO GIVE
>>>> FEEDBACK ____>>>> *GREAT____*


>>>> *AVERAGE____*


>>>> *BAD____*


>>>>  ____


>>>>  ____


>>>>  ____


>>>> __ __


>>>> *From:* AusNOG [mailto:ausnog-bounces at lists.ausnog.net] *On Behalf
>>>> Of *Matthew VK3EVL *Sent:* Wednesday, 9 August 2017 3:13 PM *To:*
>>>> ausnog at lists.ausnog.net *Subject:* Re: [AusNOG] NextDC Melbourne -
>>>> Scheduled Power Maintenance - 15th August____>>>> __ __


>>>> What about both feeds happening on the same day at the same
>>>> time?____>>>> __ __


>>>> On 9/08/2017 2:55 PM, Shaun McGuane wrote:____


>>>>> HI Damien,____


>>>>>  ____


>>>>> My apologies that’s correct – but isn’t anyone concerned about the
>>>>> works being completed during business hours?____>>>>> What about increased loading of the active rail once one of them
>>>>> is switched off for these works?____>>>>>  ____


>>>>> Regards____


>>>>> Shaun____


>>>>>  ____


>>>>>  ____


>>>>> *From:* Damien Gardner Jnr [mailto:rendrag at rendrag.net] *Sent:*
>>>>> Wednesday, 9 August 2017 2:39 PM *To:* <ausnog at lists.ausnog.net>
>>>>> <ausnog at lists.ausnog.net>; Shaun McGuane <shaun at rackcentral.com>
>>>>> *Subject:* Re: [AusNOG] NextDC Melbourne - Scheduled Power
>>>>> Maintenance - 15th August____>>>>>  ____


>>>>> It says 7am -> 4pm in what you quoted? (UTC+10 is AEST)____


>>>>>  ____


>>>>> On Wed, 9 Aug 2017 at 2:36 pm, Shaun McGuane
>>>>> <shaun at rackcentral.com> wrote:____>>>>>> HI Noggers,____


>>>>>>  ____


>>>>>> Has anyone seen this scheduled maintenance notification happening
>>>>>> next week?____>>>>>> They maybe upgrading feeds or boards throughout the datacentre –
>>>>>> has everyone seen this notification of works?____>>>>>> It appears to be happening starting 5PM through to 2AM AEST for
>>>>>> all Datahalls on the same date.____>>>>>>  ____


>>>>>>  ____


>>>>>> *WHAT:*
>>>>>> NEXTDC M1 Melbourne data centre, with the assistance of
>>>>>> specialist contractors, will conduct offline preventative
>>>>>> electrical maintenance work on high-voltage and low-voltage main
>>>>>> isolators. This will affect A and B feeds to the racks in Data
>>>>>> Hall 2/3/4 on the 15th of August.
>>>>>>
>>>>>> *WHEN:* A Feed - Tuesday 15th August 2017 07:00 UTC +10 until
>>>>>> 16:00 UTC +10. B Feed - Tuesday 15th August 2017 07:00 UTC +10
>>>>>> until 16:00 UTC +10.>>>>>> 
>>>>>> *HOW AM I AFFECTED?* Due to the nature of the work a single feed
>>>>>> will be removed as per the dates and times above. We recommend
>>>>>> that customers balance the power between both power rails to
>>>>>> minimise impact during this period. If you have single feed
>>>>>> devices we recommend you:____>>>>>>  ____


>>>>>> Regards____


>>>>>> Shaun____


>>>>>>  ____


>>>>>>  ____


>>>>>>  ____


>>>>>> _______________________________________________
>>>>>>  AusNOG mailing list
>>>>>> AusNOG at lists.ausnog.net
>>>>>> http://lists.ausnog.net/mailman/listinfo/ausnog____


>>>>> -- ____


>>>>> Damien Gardner Jnr
>>>>>  VK2TDG. Dip EE. GradIEAust
>>>>> rendrag at rendrag.net -  http://www.rendrag.net/_
_--
>>>>>  We rode on the winds of the rising storm,
>>>>>   We ran to the sounds of thunder.
>>>>>  We danced among the lightning bolts,
>>>>>   and tore the world asunder____


>>>>> 
>>>>> ____


>>>>> ___________________________________________________
>>>>> AusNOG mailing list____ AusNOG at lists.ausnog.net____
>>>>> http://lists.ausnog.net/mailman/listinfo/ausnog____>>>> __ __


>>>>
>>>> MESSAGE PROTECTED BY  *PREMIER TECHNOLOGY SOLUTIONS*[1] - POWERED
>>>> BY  *MAILGUARD*[2].  Report this message as spam[3]
>>>>   ____>>>>
>>>> MESSAGE PROTECTED BY  *PREMIER TECHNOLOGY SOLUTIONS*[4] - POWERED
>>>> BY  *MAILGUARD*[5].
>>>>   ____>>>> 
>>>> _______________________________________________
>>>>  AusNOG mailing list
>>>> AusNOG at lists.ausnog.net
>>>> http://lists.ausnog.net/mailman/listinfo/ausnog
>>>> 
> _________________________________________________
> AusNOG mailing list
> AusNOG at lists.ausnog.net
> http://lists.ausnog.net/mailman/listinfo/ausnog


Links:

  1. http://www.premiertech.com.au
  2. http://www.mailguard.com.au/mg
  3. https://console.mailguard.com.au/ras/1RqQHQIE5J/6DWUZjiMDnlts7JYyCLNB3/0
  4. http://www.premiertech.com.au
  5. http://www.mailguard.com.au/mg
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.ausnog.net/pipermail/ausnog/attachments/20170810/7eff6cb5/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 3738 bytes
Desc: not available
URL: <http://lists.ausnog.net/pipermail/ausnog/attachments/20170810/7eff6cb5/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 3778 bytes
Desc: not available
URL: <http://lists.ausnog.net/pipermail/ausnog/attachments/20170810/7eff6cb5/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 4714 bytes
Desc: not available
URL: <http://lists.ausnog.net/pipermail/ausnog/attachments/20170810/7eff6cb5/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 3771 bytes
Desc: not available
URL: <http://lists.ausnog.net/pipermail/ausnog/attachments/20170810/7eff6cb5/attachment-0007.png>


More information about the AusNOG mailing list