[AusNOG] Hypoxic Fire Suppression [was Global Switch]
Matt Perkins
matt at spectrum.com.au
Mon Jan 13 21:21:02 EST 2014
These guys seem to have installed a Hypoxic system recently. Would there
environment be small enough to meet the fresh air ingress requirements
or would the system just be running all the time in a battle between the
fresh air and putting converting it with nitrogen.
http://aragroupblog.com.au/?p=2420
On 13/01/14 8:54 PM, Tony de Francesco wrote:
>
> Just to clarify the australian BCA requirements: all habitable spaces
> including machine rooms, switchrooms, etc. must be provided with fresh
> outside air. The levels required are stipulated in AS1668 but
> typically work out at around 1 l/s per m2 for most data centre spaces.
>
> Hospital operating theatres are actually provided with 100% outside
> air via HEPA filtration with surrounding service corridors kept at
> approx -ve 20Pa pressure to ensure that no "dirty" air enters the theatre.
>
> Even if it was not a BCA requirement there is a need for fresh outside
> air in a data centre keep ot at a higher pressure than surround areas
> to ensure that "dirty" air does not enter the technical space.
>
> Regards
>
> Tony de Francesco
> Technical Director
> P.U.E. Pty Ltd
> Mob: +61 (0) 457 701 179
> Email: tonyd at pue.com.au <mailto:tonyd at pue.com.au>
>
> On 13/01/2014 8:13 PM, "Matt Perkins" <matt at spectrum.com.au
> <mailto:matt at spectrum.com.au>> wrote:
>
> That's good info Bevan,
> I wonder if the building code requires that fresh air be injected
> into the entire building or all rooms within the building. I
> wonder if Hypoxic fire prevention could be employed in small
> computer room type environments or data centers where division
> into smaller rooms or where cold/hot aisle for example. I guess
> not useful information for centers with large floor plates but may
> be useful in power room environments or small server rooms etc.
> If the building code allows.
>
> Operating theaters for example dont have fresh air injected into
> them. It's a highly filtered air that's injected from the outer
> rooms surrounding the theater through HEPA and active charcoal.
> What counts as fresh air.
>
> These guys make an interesting device.
> http://altitudetraining.com/prevenex/products/airunit
>
> Matt.
>
>
> On 13/01/14 7:07 PM, Bevan Slattery wrote:
>>
>>
>> From: Tony de Francesco <tonyd at pue.com.au <mailto:tonyd at pue.com.au>>
>>
>> > Yes but Inergen is not used in large DCs because of the volume required.
>>
>> Simply not correct. Most large DC’s segregate spaces to allow
>> full discharge in a specific area.
>>
>> > The European system is a hypoxic system at low pressure. Very different to dumping a whole bunch
>> of gas through high pressure nozzles.
>>
>> Challenge with this system in Australia (which I looked at early
>> in NEXTDC days) was that in Australia you need to continually
>> supply fresh air to a DC under the building code. It is
>> difficult to continually deliver a hypoxic environment across a
>> large facility considering the Australian standards and the need
>> to continually extract O2/Inject N2 into the air supply.
>>
>> Hypoxic systems are typically used in things like ship engine
>> rooms to reduce the risk of catastrophic fire or in environments
>> with low traffic flow (archives). In a colocation environment in
>> Australia I couldn’t get an insurer to get their head around
>> having staff and customers in a facility with a reduced O2, let
>> alone the technical issues around a requirement to continually
>> alter the air mix due to the building code.
>>
>> So if you want to maintain a lower level of O2 you had to operate
>> the Agent Generator (essentially lower O2 in a bottle) 24/7 to
>> maintain the O2 levels at the Fire Type 2 levels. The amount of
>> fresh air required in a 20,000m facility that had a volumetric
>> size of 100 megalitres is “significant”. Very significant.
>>
>> All in all it wasn’t technically or commercially viable for
>> NEXTDC at the time to provide a continuous hypoxic environment.
>> This may have changed. There was some investigation into using
>> an agent generator to create the refill in case of discharge
>> removing the need for a refill from alternate gas suppliers. But
>> the equipment needed to refill 20 megalitres (hall discharge +1)
>> was significant and the bottles required was considerably greater
>> from memory. Also not all gas discharge systems are as high
>> pressure these days so you may want to check out the latest to
>> ensure your points are valid.
>>
>> Cheers
>>
>> [b]
>>
>>
>>
>>
>>
>>
>> _______________________________________________
>> AusNOG mailing list
>> AusNOG at lists.ausnog.net <mailto:AusNOG at lists.ausnog.net>
>> http://lists.ausnog.net/mailman/listinfo/ausnog
>
>
> _______________________________________________
> AusNOG mailing list
> AusNOG at lists.ausnog.net <mailto:AusNOG at lists.ausnog.net>
> http://lists.ausnog.net/mailman/listinfo/ausnog
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.ausnog.net/pipermail/ausnog/attachments/20140113/973ba361/attachment.html>
More information about the AusNOG
mailing list