On 12/16/10 4:31 PM, Trent Lloyd wrote:
> I've run a 2.2KVA UPS on house power for a few years as have many
> associates of mine and not had any issues through brownouts, black
> outs, overvoltages, etc causing a trip.
>
> Have you actually run into this issue of it breaking in real life?
I have seen this happen, not necessarily in Australia, but elsewhere.
2.2KVA is well within the safe limits compared to the 3KVA. Some
mathematics.
10A power draw at 220-240V would be 2200-2400W. 2200W is the typical
Australian power supply. .
A 2.2KVA UPS with power factor of .8 (typical with UPS) would draw 1760W.
A 3KVA UPS with power factor of .8 would draw 2400W.
So, while the 2.2KVA UPS is in a safe bracket, with the 3KVA its on
marginal grounds.
- -gaurab
- --