<pre wrap="">I agree with you about the current only showing if there is a fault in the main board.
I also have some racks with rack mounted satellite RF comm's gear that I want to make sure that I don't have transient RF increasing the noise floor, so I'll take the extra earthing for those systems..
Here is a question thou, say I have a secondary UPS (Bottom of rack UPS e.g <span class="small-desc">Liebert GXT3</span>), what happens if these go electrically bad ?.. For me I'm hoping that the extra rack bonded earth also takes care of those problems..
Cheers
Greg
</pre>
<br>
<div class="moz-cite-prefix">On 21/06/2016 8:15 PM, John Lindsay
wrote:<br>
</div>
<blockquote cite="mid:07B94B82-A6F9-4D89-AE98-90CE70930D53@mac.com"
type="cite">
<pre wrap="">On upon a time RCDs weren’t required for sockets at 20 amp and up.
That rule appears to have changed.
By rule I mean interpretation of the standard.
I saw some three phase EV charging points being installed recently and the electrician said that “new rules” required him to install RCDs in line with them. That’s mildly amusing because the charging units themselves have much better RCD function than the clunky and expensive electromechanical units he was installing.
BTW, you would only see current in that separate earth connection if the earthing at the sub board and main board were to fail because the path to “ground” would likely be much low resistance via the neutral block in the main board.
Cheers,
jsl
John Lindsay
<a class="moz-txt-link-abbreviated" href="mailto:johnslindsay@mac.com">johnslindsay@mac.com</a>
+61403577711
</pre>
<blockquote type="cite">
<pre wrap="">On 21 Jun 2016, at 7:01 PM, Greg <a class="moz-txt-link-rfc2396E" href="mailto:mclennan@internode.on.net"><mclennan@internode.on.net></a> wrote:
In a small (24 rack area) I look after. We have no RCD's inline for our under floor 20/32Amp rack-power sockets. However I separately earth each rack to a common earth that all runs to a separate large earth stake that runs outside the facility to help mitigate a 'live' rack incident. On reflection of that setup, I suspect I could add in a current detection device to that separate earth to make me aware that one of the racks got an issue since there is no RCD..
Cheers
Greg
On 21/06/2016 6:59 PM, Brad Peczka wrote:
</pre>
<blockquote type="cite">
<pre wrap="">Hello All,
For those on list who run data centres, either in house or as a commercial operation like NextDC/Metronode - can anyone shed some light on the requirements (or lack thereof) for RCD protection within a Data Centre?
My experience in the past has been that, where PDUs are connected via 32A sockets or similar, RCDs are not required. That being said, an interesting presentation a few years back from the folks at CITEC (<a class="moz-txt-link-freetext" href="http://www.server-racks-australia.com.au/News_articles/Residual%20Current%20Protection%20in%20the%20Data%20Centre%20DM.pdf">http://www.server-racks-australia.com.au/News_articles/Residual%20Current%20Protection%20in%20the%20Data%20Centre%20DM.pdf</a>) would seem to indicate that this is not the case, and that their interpretation of AS3000:2007 requires RCDs to be fitted to or upstream from PDUs. The installation of emergency stops for facility power also seems to be very hit and miss, and varies depending on when/where and who.
I'm curious to know if this is a common view and, if not, how others are handling electrical safety within Data Centres/Comms Rooms/Server Rooms.
Regards,
-Brad.
_______________________________________________
AusNOG mailing list
<a class="moz-txt-link-abbreviated" href="mailto:AusNOG@lists.ausnog.net">AusNOG@lists.ausnog.net</a>
<a class="moz-txt-link-freetext" href="http://lists.ausnog.net/mailman/listinfo/ausnog">http://lists.ausnog.net/mailman/listinfo/ausnog</a>
</pre>
</blockquote>
<pre wrap="">
_______________________________________________
AusNOG mailing list
<a class="moz-txt-link-abbreviated" href="mailto:AusNOG@lists.ausnog.net">AusNOG@lists.ausnog.net</a>
<a class="moz-txt-link-freetext" href="http://lists.ausnog.net/mailman/listinfo/ausnog">http://lists.ausnog.net/mailman/listinfo/ausnog</a>
</pre>
</blockquote>
<pre wrap="">
</pre>
</blockquote>
<br>
</body>
</html>