<div dir="ltr">What kind of optic?  Assume LR in a DC on SM.  10GBaseLR has an optical budget less than 10dB, so -19dBm should be triggering low power alarms.<div>Inside a building I'd expect to see under 4dB loss - will depend a lot of patching (is it a single cable or lots of bulkheads as you pass through a MMR or many of them).<br></div><div><br></div><div>(SMF is 0.1dB per Km with splices, patches more (usually considered 1dB) - hence why inside a building is going to be a bit higher if lots of patching).</div><div><br></div><div>I'd fault whoever is providing you the patch.</div><div><br></div><div>MMC</div></div><div class="gmail_extra"><br><div class="gmail_quote">On Thu, Aug 27, 2015 at 10:30 PM, Robert Hudson <span dir="ltr"><<a href="mailto:hudrob@gmail.com" target="_blank">hudrob@gmail.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><p dir="ltr">Hi all,</p>
<p dir="ltr">What level of loss should I accept on a single mode cross connect in a DC?</p>
<p dir="ltr">I have a dark fibre link measured as <4dBm end-to-end over a 13km run, but am seeing 19dBm switch-to-switch in both directions.</p>
<p dir="ltr">Thanks!</p>