[AusNOG] FW: Transgrid Power Dip - Global Switch Generators Momentarily take Building Load

Jason Ashton jason at bigair.net.au
Thu Jul 2 11:41:55 EST 2009


I would guess that Equinix was affected by power issues which affected
large areas of Sydney (we noticed some customer sites down). 

 

As per below Global Switch Ops also noticed the outage but they were not
affected.

 

cheers,

Jason

 

 

Jason Ashton 
Chief Executive Officer

BigAir Group Limited

email: jason at bigair.net.au | address: Level 1 / 59 Buckingham St, Surry
Hills, NSW 2010 
main: +61-2-99931300 | direct: +61-2-99931316 | fax: +61-2-80808162 |
mob: +61-411-757776 

 

 

 

From: Kevin Ross [mailto:kross at globalswitch.com.au] 
Sent: Thursday, 2 July 2009 11:39 AM
To: undisclosed-recipients
Subject: Transgrid Power Dip - Global Switch Generators Momentarily take
Building Load

 

Dear Client 

 

At approximately 10:48 today the incoming 33kV main supplies fed from
the Transgrid network experienced a dip in voltage of sufficient level
to initiate an automatic start of the generators. The generators took
the build load with ease and following the programmed minimum run time
of 5 minutes, to confirm the stability of the incoming supply, the
automatic shut down sequence was initiated which returned the building
to mains supply. During this period the no break and short breaker
supplies were maintained as designed with no system operational issues
noted. 

 

Regards

 

Kevin Ross 

Operations Manager

GLOBAL SWITCH 
400 Harris Street, Ultimo NSW 2007 
T  +61 2 9566-7000   F +61 2 9566-7032 
M +61 0458 230 025  D +61 2 9566-7006
Email kross at globalswitch.com.au 

This email is sent to you from Global Switch. Full details of the Global
Switch Group, its ultimate parent company, and its country operating
companies, can be found on our web site at www.globalswitch.com

The information in this e-mail and any files transmitted with it are
confidential, may be privileged or otherwise protected from disclosure,
and are intended for the named recipient. If you are not the intended
recipient you must not use the information in this e-mail or any files
transmitted with it, must delete it from your system, and should inform
us immediately using the contact details above.

 